If bonding is required then it does not get carried thru t the disconnect. IMO, that would be a violation of parallelling the neutral. One would think metal conduit would also be a violation in this case but for some reason it is not.When bonding the galvinized rigid nipple beween the meter pan and 200A service panel, do we need to carry the bonding wire thru to the meter pan or do we just connected the bond wire to the bonding bushing in the service panel?
Yes, the intent is to ground the metal nipple, which you only have to do in one location.
Panel side only.
Leo, what do you mean by "panel side only"?