Hendrix
Senior Member
- Location
- New England
What size conductors would your poco run ??
What size conductors would your poco run ??
It is an 8 tennant apt house.Whatever size they choose would have nothing to do with the 600 amp breaker or NEC calculations, it will be based on what they know the building will require.
If poco owns it, they can run what they want. 90.2(B)(5) Hopefully it will be of sufficient size. Whatever that means.:roll:What size conductors would your poco run ??
If poco owns it, they can run what they want. 90.2(B)(5) Hopefully it will be of sufficient size. Whatever that means.:roll:
OK, what if the electrician runs the cable, 310.16 ?If poco owns it, they can run what they want. 90.2(B)(5) Hopefully it will be of sufficient size. Whatever that means.:roll:
Actually I think you only need to run a wire based on the calculated load for the lateral. I hope that's right.OK, what if the electrician runs the cable, 310.16 ?
If it was done by an electrician, I think that it would need 750kcm paralleled cu.I did a 600 a few months ago and they ran 500 AL
If it was done by an electrician, I think that it would need 750kcm paralleled cu.
230.42 Minimum Size and Rating.
(A) General. The ampacity of the service-entrance conductors before the application of any adjustment or correction factors shall not be less than either (A)(1) or (A)(2). Loads shall be determined in accordance with Part III, IV, or V of Article 220, as applicable. Ampacity shall be determined from 310.15. The maximum allowable current of busways shall be that value for which the busway has been listed or labeled.
(1) The sum of the noncontinuous loads plus 125 percent of continuous loads
(2) The sum of the noncontinuous load plus the continuous load if the service-entrance conductors terminate in an overcurrent device where both the overcurrent device and its assembly are listed for operation at 100 percent of their rating
Thank you for the info You didn't seem that sure yourself:grin:Actually I think you only need to run a wire based on the calculated load for the lateral. I hope that's right.
Simple, in my town, any 1 ph. service over 225 amps & all 3 ph. services have to have an engineer's stamp. Therefore, the electrician will have to run the size spec'd by the EE.OK, what if the electrician runs the cable, 310.16 ?
That could get very costly :roll:Simple, in my town, any 1 ph. service over 225 amps & all 3 ph. services have to have an engineer's stamp. Therefore, the electrician will have to run the size spec'd by the EE.
How's that for dodging your question?:grin:
We would have to fill out a load data sheet and they would use that for sizing the transformer and the conductors.
They could use what we consider small conductors, I know of one 600 amp service close by fed with 3/0.
Roger
If it was done by an electrician, I think that it would need 750kcm paralleled cu.
Around here, the POCO sizes the conductors based on their historical data of power consumption for a particular occupancy. I too have seen 200 amp single phase fed with 1/0 aluminum.