windandsun
Member
- Location
- SE Michigan
We have a customer that requires RMC wherever raceway is used on the rooftop. We will be installing several islands of photovoltaic panels on the roof, which must be grounded, as well as the raceway, (per 690.43). The wiring beneath the modules will be exposed USE-2 (as permitted in 690.31 (B)), but the wiring will be in RMC where run between islands of modules. I had planned on using bonding bushings to comply with 690.43, where the RMC runs between islands of modules, but I can't find any that are listed for use in wet locations. Does anyone know of any type of mechanical grounding or bonding clamps that can connect bare solid 8 AWG to RMC (conduit sizes are from 1/2" to 1 1/4")?
Thanks, Wes
Thanks, Wes