But, unlike kitchen SABC receptacles, it doesn't say that every receptacle in the bathroom must be on a 20a bath-receptacle-only circuit.
It must still be GFCI-protected, of course.
That's the way I'd go with this. Time for another Poll? :grin:
If the code allows lighting to be on the circuit with the bath recep if the circuit doesn't leave that room then what would be the problem with allowing a recep. that is not part of the required recep by the sink to be on with the lighting.
Again is a washing machine allowed in a bathroom-- mine is.Of course it is on a separate 20 amp circuit but a better case would be a switched outlet for a picture light or lamp. I have done this and as long as it is GFCI protected I believe it is okay.
If this recep. was added after inspection then I wouldn't bother calling the inspector but for future installs it may be worth checking with the ahj.
In that case, yes.So I am doing a bathroom on the second floor of a cape cod and I have already run my bath GFCI, can i run my lighting for my bath on that line to? This is the only bath on this line.
As mentioned above I disagree with the fact that you cannot have another recep. in the bathroom unless it is on the bathroom required circuit. If that were true then you could not have a washing machine in a bathroom.
Bathroom. An area including a basin with one or more of the following: a toilet, a tub, or a shower.
(1) [OSHPD 1, 2 & 4] Receptacles shall not be installed within shower rooms or stalls or be accessible from within these areas. Receptacles shall not be installed within 5 feet (1.52 m) of the perimeter of bathtubs.
So I am doing a bathroom on the second floor of a cape cod and I have already run my bath GFCI, can i run my lighting for my bath on that line to? This is the only bath on this line. I was going to run the bath lighting off of the general lighting but that would be a real PITA (most of the second floor is already finished) this would save me a lot.
I disagree. I never refer to my bathroom as the laundry room it is simply a bathroom with the laundry equipment. There is no definition for laundry room but there is for a bathroom, thus this is a bthroom and not a laundry room with a bathroom in it. IMO.And if there was a washer and dryer in the bathroom that area containing the laundry equipment is the laundry area and not a bathroom IMO.
Just don't forget to run #12 to your lights in that bathroom!:grin:
I have been interpreting the code as requiring all bathroom recepts to be on the 20A circuit, but now I wonder! I once old-worked a receptacle in a bathroom next to the toilet for a client. She had a lamp or something there and had been running a cord into her master bedroom. I took power from a receptacle in the bedroom that was back-to- back in the same stud space and used a GFI recept. At the time, I told her this was a code violation, but safer than the cord situation. Now I feel better about the whole thing and will be able to sleep nights! Thanks Larry!
I was under the impression that you could take #14nm to the lights from a switch box that is supplied with #12nm. We always do it here and never had any inspection problems.
What is that circuit your putting 14G on protected for 15 or 20Aon what size breaker ?
It is feed with a 20amp breaker. But they allow us to install 14-2 to the lights from the switch box when the HR is a 12-2
I figured it wasnt nec acceptable but our local ahj still allows it.
just curious--where is it that they are allowing this?I was under the impression that you could take #14nm to the lights from a switch box that is supplied with #12nm. We always do it here and never had any inspection problems.
Okay I get it, a bathroom is not a room :roll:. I really didn't think that something called a Bath ROOM needed to be defined as a room. IMO, the bathroom contains the laundry equipment and your thinking would never fly in this area. Perhaps it would where you are.I did not say your bathroom is a laundry room, I said the area containing the laundry equipment is the laundry area and that the code does not define a bathroom as a room but as an area.
Just because you 'have not had any problems' if suppying this on a 20A breaker - it still is a violation of 240.4 - just means your inspectors are not paying attention.I was under the impression that you could take #14nm to the lights from a switch box that is supplied with #12nm. We always do it here and never had any inspection problems.