The building which contains our offices and shops is served by a 1200 amp 120/208 wye service.  We are going to install a 300 KW standby generator to pick up the entire building.  2 years of demand and KW readings verifies our load doesn't exceed 210 KW (about 580 amps) so the 300 KW generator should be fine.  My plan is to install an 800 amp service rated fused disconnect between the utility transformer and the ATS switch.  The generator also has an 800 amp overcurrent device which will feed the other side of the transfer switch.  I am planning on paralleling 3-300 MCM Aluminum conductors from the generator and transformer to the ATS as well as from the ATS to the building service.  The one issue that I wonder about is the 1200 amp disconnect on the building service (which I plan to convert to 4 wire).  Do you see any issue with the existing OC device remaining at 1200 amp?  Although leaving the 1200 in place might be confusing, it appears all conductors and equipment will be adequately protected.  Changing out this OC device would probably be around $5000 so I am trying to avoid that.  Any thoughts?