During a fault the bare can arc & spark to the rigid conduit causing damage to the ungrounded & grounded conductors in multible places that may not have happened with an insulated EGC.
Watch for solid -vs- stranded though. Many people seem to buy bare in solid. You can't pull solid wire larger than #10 through a raceway.
other than it not being manufactured/made in solid larger than 10.
I use #4 solid all the time. You just can't put it in a raceway except as a sleeve.What code article is that? other than it not being manufactured/made in solid larger than 10.
I believe you have to bond both ends if it is a GEC in metal conduit.If the bare EGC and pipe were bonded at both ends, would you have arcing between them?
Supposedly if the conduit is bonded it will prevent the choke effect. Don't ask me what it is but here is a little info from our forum on the choke effect.Yes, so would it really arc??
That is possible where very high AC currents are flowing on a single conductor (no other conductors in the same raceway) installed in a ferrous raceway.I was under the assumtion that, under a fault condition, a bare conductor would literally be cut in half at the piont in penetrates an unbonded raceway.
We buy solid up to #2.
Roger
If they are bonded together they are the same potential - why should they arc?
There would be a difference of potential between the bare EGC and the conduit during fault conditions.
If that was enough to make a damaging arc is a crap shoot in my opinion.