S session88 Member Location USA Sep 2, 2010 #1 Is it a code violation to change sizes in the middle of a conduit run (rigid)? Or is it just a bad practice to do so?
J jusme123 Senior Member Location NY Occupation JW Sep 2, 2010 #2 session88 said: Is it a code violation to change sizes in the middle of a conduit run (rigid)? Or is it just a bad practice to do so? Click to expand... No its not against code, in fact, its done quit often if you are referring to less conductors as the conduit run continues
iwire Moderator Staff member Location Massachusetts Sep 2, 2010 #3 The NEC does not prohibit changing sizes in the middle of a run of course that assumes you maintain proper conductor fill for the smaller raceway.
S session88 Member Location USA Sep 3, 2010 #4 So it is ok to reduce a conduit size in the middle of a run at a coupling with an RE bushing, or is a condulet or j-box required when changing sizes?
Split Bolt Senior Member Location Northern Virginia Sep 3, 2010 #5 Didn't drag the NEC out, but I would think it's OK in the middle of the run. They make all kinds of neat adapters for this in PVC.
N nakulak Senior Member Sep 3, 2010 #6 not a violation. depending on the application, might be bad practice (but not always)