Changing conduit size
session88
USA
Is it a code violation to change sizes in the middle of a conduit run (rigid)?
Or is it just a bad practice to do so?
No its not against code, in fact, its done quit often if you are referring to less conductors as the conduit run continues
The NEC does not prohibit changing sizes in the middle of a run of course that assumes you maintain proper conductor fill for the smaller raceway.
So it is ok to reduce a conduit size in the middle of a run at a coupling with an RE bushing, or is a condulet or j-box required when changing sizes?