I woul say that the intent of the two pole AFCI Breakers are 240 volt loads like window A/C and Electric baseboard heat.
I don't think that running MWBC for 120 volt loads is a good idea but if you do
you need a two pole AFCI breakers
Actually, that was my whole point-I don't like MWBCs for 120 volt branch circuits, for previously stated reasons. I prefer one hot, one neutral, one ground.
If supplying an
individual branch circuit of 240, 120/240 or 120/208 volt, to single-or 3-phase loads, that's
completely different. I'd never put a 120 volt load on one side of an existing 120/240 3-wire 15-or 20-amp MWBC.
I'm no genius, nor am I an engineer. I'm just a sparky. So yeah, I
do listen to the 'so called experts'.
None of my installations ever caused fire or injury (I started in 1986- GFCI's were only used outdoors and in bathrooms, and nobody had heard of AFCIs). Always believed careful craftsmanship is the cornerstone of safe, long lasting installations. I'm preaching to the choir here.
Are electrical systems safer now (with AFCIs and GFCIs) then in 1986? I don't think they're less safe.