Call from customer today stating they witnessed a large flash or ball of fire early this morning from behind a three inch rigid conduit. 480v to 250hp motor via softstart. Nothing tripped. Ok. Sure enough there is an obvious spot on the conduit. Sound like a faulted conductor? Nothing burned thru like I would expect. Not sure of the protection abilities of the softstart but I would have expected it to fault out.
We megged it, with one set of paralells not reaching the same level as the other sets. 1780 meg vs 2G. Manager said run, so they are. I expect a large hole the next time.