- Location
- San Francisco Bay Area, CA, USA
- Occupation
- Electrical Engineer
... Would the heating of this conduit during a brief fault cause the conduit to get hot and bright enough to cause the flash they saw?
In a word, no.
An insulation failure and arcing fault to ground in one conductor inside that conduit, maybe. Hence the concern we all express. Problems like that don't just go away, they get worse.
Look, you megged the cable and found an anomaly, as distasteful as it sounds you have to get to the root of the problem and most likely replace that cable. MAYBE if you can pull it back a short distance to a J-Box somewhere you might be able to get a wrap-around repair sleeve on it. But that opens up the risk of nicking it somewhere else, or another cable with it. Plus are there other conductors in that conduit? If so, they were most likely damaged as well. Cable insulation has a much lower temperature damage threshold than RGC, if that burn mark came from the inside, there is major damage in there.