Is the calculated load on a 150watt HPS just a straight 150W? At 120v volts it would be .8 amps?
 

480sparky

Senior Member
Location
Iowegia
2 amps? go to fix manuf. for cut sheet info.

smiley-winner.gif

 

dicklaxt

Senior Member
120/208/240/277 ballasts have operating currents of 1.8/1/.9/.8 respectively,,this current is what is used for circuit loading,the socket voltage oft times does not vary even tho the wattage may.............480V is .4 amps if you need that.

dick
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
And, don't forget to cap those other voltage taps. Each puts out its labeled voltage when any one is supplied at its voltage. The primary is an auto-transformer.
 

LEO2854

Esteemed Member
Location
Ma
And, don't forget to cap those other voltage taps. Each puts out its labeled voltage when any one is supplied at its voltage. The primary is an auto-transformer.

yes there is nothing like reaching in the fixture and touching an uncapped 277volt leed .zzzzz:roll:
 