Is the calculated load on a 150watt HPS just a straight 150W? At 120v volts it would be .8 amps?
 
2 amps? go to fix manuf. for cut sheet info.

smiley-winner.gif

 
120/208/240/277 ballasts have operating currents of 1.8/1/.9/.8 respectively,,this current is what is used for circuit loading,the socket voltage oft times does not vary even tho the wattage may.............480V is .4 amps if you need that.

dick
 
And, don't forget to cap those other voltage taps. Each puts out its labeled voltage when any one is supplied at its voltage. The primary is an auto-transformer.
 
And, don't forget to cap those other voltage taps. Each puts out its labeled voltage when any one is supplied at its voltage. The primary is an auto-transformer.

yes there is nothing like reaching in the fixture and touching an uncapped 277volt leed .zzzzz:roll:
 