Machiavelli999
Got into a pretty heated argument recently with a colleague and hoping that you guys can help clear this up.
First, a 480 - 208/120V delta-wye transformer is being installed and is being fed on the primary side from a switchboard breaker. On the secondary side, is another breaker necessary? I said yes and in the NEC Article 240.4(F) it says it pretty explicitly
"Single-phase and multiphase transformer secondary conductors shall not be considered to be protected by the primary overcurrent protective device"
There are a couple of exceptions given (a single-phase 2 wire or a delta-delta 3 phase transformer can be considered protected on the secondary side just by having a primary breaker) but it seems pretty clear that secondary breaker is needed.
The second question is for an Automatic Transfer Switches, if I have a breaker protecting the Normal feeder and the Emergency feeder, do I need a breaker to protect the Load feeder. My colleague says no. I think yes, but I am not as sure about this one. Couldn't find anything in the code about this.