zbang
Senior Member
- Location
- Roughly 5346 miles from Earls Court
IMHO-
Generator is the SDS, it has a bonding jumper, might have GES (which is arguable).
Panel is (loosely) utilization requirement, never a bonding jumper. Whether it has a GES is also arguable. (At least, none of the UL listed temp power gear I have has a jumper.)
End utilization equipment, doesn't need a GES, but that won't hurt anything.
As long as all the grounding electrodes are tied to the same grounding system, I don't see a problem.
	
		
			
		
		
	
				
			Generator is the SDS, it has a bonding jumper, might have GES (which is arguable).
Panel is (loosely) utilization requirement, never a bonding jumper. Whether it has a GES is also arguable. (At least, none of the UL listed temp power gear I have has a jumper.)
End utilization equipment, doesn't need a GES, but that won't hurt anything.
As long as all the grounding electrodes are tied to the same grounding system, I don't see a problem.
 
				
 
 
		 
 
		 
 
		 
 
		