Yes it is required . Look at article 680.26Is an equipotential bonding grid required on self contained hot tub set on an outside existing concrete deck and how can it be installed?
Dennis answered the why but the how is the real question. :roll:
Which code cycle are you referencing?
2008 NEC. You can not just post 2008 NEC. You must post at least 10 characters.
When that happen to me, I do this
2008 NEC..................
when that happen to me, i do this
2008 nec..................
Unless this is the hot tun from hell, all you need in virtually every case is #8 or #6 wire run to a GFCI protected spa disconnect, followed by a whip run directly to the electrical cabinet inside the hot-tub. I admit that I've only done about 200 spas, but wow! What are you going to bond? There's a ground clamp in the electrical enclosure and spaces for two hots and a neutral! The hot tub is pre-bonded by the manufacturer! Just post a copy of the instaqllation instructions nect to the permit so the inspector can see it!
A self contained hot tub is manufactured of fiberglass, rubber, plastic, wood and very little metal. A bonding grid is required when you have a pool with a metal structure that is not necessarily bonded together. I've done a couple of French made pools wher ethe entire structure was seperate metal supports with no common link between them. We had to bond every single metal part. Unless this is the hot tun from hell, all you need in virtually every case is #8 or #6 wire run to a GFCI protected spa disconnect, followed by a whip run directly to the electrical cabinet inside the hot-tub. I admit that I've only done about 200 spas, but wow! What are you going to bond? There's a ground clamp in the electrical enclosure and spaces for two hots and a neutral! The hot tub is pre-bonded by the manufacturer! Just post a copy of the instaqllation instructions nect to the permit so the inspector can see it!
"But wow" either you don't know the code or the Inspector doesn't, or the install is not being inspected!
680.26 refers to Permanently Installed Pools (Part II). Portable Spas fall under Part IV and are subject to Part I and Part II. Bonding is required for certain components but there is no requirement for an equipotential bonding grid that I can find.
Oops. My bad. I should have wrote: Portable spas are subject to Part I and Part IV - not Part II. 680.26 is in Part II. So I would read that no equipotential bonding grid is required. Sorry about that...
680.42 Outdoor Installations.
A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and (B), that would otherwise apply to pools installed outdoors.