ceb58
 - Raeford, NC
I have two scenarios to present on wiring in a COPS plug for a gen. to supplement a permanently installed gen. in case of failure.
The first way this set up was wired. Normal utility lands on N1,N2 in ATS, permanent gen. wire from disco. lands on E1,E2 in ATS, T1,T2 wire from ATS goes to top lugs in a manual gen. switch. Wire on center lugs(common) goes to MDP. Wire on bottom lugs go to female COPS plug.
With this set up if the permanent gen. goes out and a portable is brought in power will be routed to the MDP with out energising any thing in the ATS which would be good if there were a need to work in the ATS ( change transformer, work on contactor, ETC...)
The second way I am being ask to wire it is.....
Wire from permanent gen. disco lands on top lugs in manual switch, wire from center lugs(common) go to E1,E2 in ATS, wire from bottom lugs go to the female COPS plug.
This way if the permanent gen. goes out and a portable is brought in it will power the emergency side of the ATS which will cause it to transfer like normal.
Some where in the second scenario I think there are some code violations but 708.24 is not clear. The main thing I see is if the problem is in the ATS then the switch will be hot. If the problem is in the contactor or transformers in the ATS then the power will have to be removed to work on it thus making the whole set up useless. Any other code violations with the second setup?