equipotential bonding grid
I posed this same question with my AHJ awhile back. According to him, the self contained portable spa is "listed equipment" and not required to be attached to a ebg.
What year NEC are you referring to?
If you take a look at Part IV of Art 680, you will see 680.42. (2008 NEC)
680.42(B) State the bonding of bands/hoops are not required to be bonded as per 680.26. This does not mean the hottub/spa is exempt from the requirements of 680.26.
**Charlies Rules is a very well written statement of how to deal with the NEC. I actually think it works well for all codes.
Here is a small portion of his words:
"It doesn't say what you think it says, nor what you remember it to have said, nor what you were told that it says, ..."
Every class I teach gets a copy of this, and I explain it to them. If you want the entire language, I will post it.