#12 good for 30 amps
When it's terminations are rated for 90? C and other restrictions do not apply. You can also use it for derating.
Welcome to the Forum. :)
Welcome to the Forum...
if I may add to my learned colleague's comments...
The post Title referred to "30 amps", the body to "actual value".
They covered the 30 amp rating, but, you might want to note that 240.4(D) which reference 240.4(E) & (G) and allows you to use the 75? rating (20 amps for 14, 25 for 12) in certain specific applications.
If I remember correctly, I think you can use these values for motors. For example heat pumps or AC units.
That is correct. As Roger stated 240.4 (G) allows you to use the actually value for a/c, motors etc. 240.4(D) is what restricts us and (G) states where it is okay to use the actual values. Thus #12 is good for 25 amps for all those items in 240.4(G).
We are allowed to do this because motor loads are better protected than normal branch circuits because of motor overload devices .
In other words. For the loads listed in 240.4 (G), you can install a conductor that is rated to carry the minimum ampacity required per the nameplate, and set the ocd at the maximum required per the nameplate.
Example: 2 ton A/C condenser nameplate
Min Amps: 19
Max Amps: 25
Install a #12 with a 25 Amp breaker.
Min Amps: 19
Max Amps: 25
Yes, but you could also use #12 for a min. cir. ampacity of 24 and still be compliant.
Min Amps: 19
Max Amps: 25
240.4(G) will lead one to 440.6, which permits this type of usage.