NCElectrician
When is #14,#12 good for ampacity of their actual value found in 310-16?
This is its rating in the 60 c chart.?
That is correct. As Roger stated 240.4 (G) allows you to use the actually value for a/c, motors etc. 240.4(D) is what restricts us and (G) states where it is okay to use the actual values. Thus #12 is good for 25 amps for all those items in 240.4(G).If I remember correctly, I think you can use these values for motors. For example heat pumps or AC units.
In other words. For the loads listed in 240.4 (G), you can install a conductor that is rated to carry the minimum ampacity required per the nameplate, and set the ocd at the maximum required per the nameplate.
Example: 2 ton A/C condenser nameplate
Min Amps: 19
Max Amps: 25
Install a #12 with a 25 Amp breaker.
Yes, but you could also use #12 for a min. cir. ampacity of 24 and still be compliant.
Min Amps: 19
Max Amps: 25