Is it allowable to backfeed a 480 delta to 120/208 wye three phase transformer? What should be done with the grounding systems?
Gee. Maybe we're right, then.Seems like this has been a common topic recently, at least every time it is asked the answers are fairly consistent with other threads on the topic.
The transformer will also have to be listed as suitable for reverse connection.
The transformer will also have to be listed as suitable for reverse connection.
Reference please.![]()
Is it allowable to backfeed a 480 delta to 120/208 wye three phase transformer? What should be done with the grounding systems?
Dont forget to take the ground strap from the XO terminal to the case off.
Okay, I'm in a similar situation and am curious what would happen if that strap were to be left in place.
Grounding the 208 side will allow unbalanced currents on the 208 system side to flow through the transformer in an effort to balance that side of the system. Lifting the strap interrupts the circuit. If you have a perfectly balanced 208 system you'll have little trouble. If your 208 side is unbalanced you might have trouble, depending on the magnitude of imbalance.
Grounding the 208 side will allow unbalanced currents on the 208 system side to flow through the transformer in an effort to balance that side of the system. Lifting the strap interrupts the circuit. If you have a perfectly balanced 208 system you'll have little trouble. If your 208 side is unbalanced you might have trouble, depending on the magnitude of imbalance.
I studied this in a graduate class longer ago than I care to admit, but have witnessed it a couple of times also.
Jim T
First off, utility MV systems behave differently than do our 480Y and 208Y systems do, so do not try to compare them..