I have worked on quite a few of these with broken/damaged operators and lubrication never did any good, typically it is a broken mechanism,.
Not to rob Zog of a sale here, but your switch has a shunt trip on it and if the shunt coil was damaged in whatever caused the original POCO outage, then it may not be releasing which would make it so that you can't charge it.
Still, from the sounds of it someone cranked that handle the wrong way and broke something.
Definitely not what happens.You should be able to charge and attempt to close it, the switch would trip free.
I think you are putting more into this than there needs to be. I have never seen instuctions on cleaning dust and crap out of a breaker, of course I have not seen everything.
In 25 yrs I have never had an issue with cleaning and re-lubing breakers mechanics. Were not talking about submersing the breaker here.:roll:
Most every large frame breaker I have seen, the springs and ratchet assembly is fully exposed just behind the front cover. I don't think we are talking about the newest electronic type breakers or MV type breakers.
Larry can do as he wishes but there is no need to sell the customer a "new" breaker if it is just dirty.
Good point. I'd hate to replace the switch and have the new one do the same thing. How does one tell?
It does, and it certainly feels like a mechanical problem. Again, how does one make sure it's not electrical?
Tony, it seems your customers would be just as well off hiring a labor or shade tree mechanic.
If I was Larry I would follow Zogs advice.
They're not even beginning to charge. When I turn the candle CCW and the back, the open button goes in slightly and the #1 moves from the window, and then they come back. We never see the #2.Gentlemen, stick with the opening post: the symptions indicate that the closing springs are not fully charging.
The customer had already replaced the other switch in the same cabinet, and has accepted the replacement idea.If this fails then replace the switch. If the customer has multiple switches then have the old one repaired and kept as a spare.
That's my plan. I've already submitted the proposal, and am hoping to hear back soon.If I was Larry I would follow Zogs advice.
Tony, let's say I try your idea. How do I find the sticking/slipping part, make sure the cleaning/lubing works, and guarantee they won't have the issue again?Just because someone lacks the knowledge to find the root cause and correct the problem in the most effecient and economical way to serve the customer is no reason to sell the customer new equipment.
Bob,
So your solution to fixing all switchgear problems is to replace the equipment?
If that is the case then I have been doing everthing wrong for 40 yrs!
PM is a big part of my business and I guess having my own business for 22 years is by dumb luck!
You all sound like ASCO salesmen to me!!!!!!!!!!!
Bob,
So your solution to fixing all switchgear problems is to replace the equipment?
If that is the case then I have been doing everthing wrong for 40 yrs!
PM is a big part of my business and I guess having my own business for
22 years is by dumb luck!
Just because someone lacks the knowledge to find the root cause and correct the problem in the most effecient and economical way to serve the customer is no reason to sell the customer new equipment.
Still waiting for approval. Tick, tock, tick, tock . . .What was/is the final outcome of the repair?
Zog, I definitely have issues with NETA, BUT............... I will save them for another post.
Tony
Sorry, I said Brian, I meant Larry Fine.Ok, let's all calm down. Bob, Zog, Brian, etc, I think we all have something to bring to the table in solving problems. We learn something every day. That is why I always come back to this forum. When I read Bob's last post it was like a revelation.....that's it!!. ...he is absolutly correct.....!!!
Do not do anything that you are not comfortable with. My reaction to Brian's problem was from the gut. Not even thinking that he was not on the same level of experience with breakers and switches. To me it is all common sense since I have been doing it for so long and know what works and what doesn't with switchgear. I am not bragging, just trying to explain things from my prospective. If someone has a different experience then I am eager to learn from him. I will (and hope all of you will) try to put a more positive approach on future posts.
Brian, my suggestion to you is to replace the switch because of the political nature of what has transpired. Without the experience and confidence in how you should proceed, I think you have no choice.
As always guys, keep the problems coming and hopefully we can resolve them in a civilized manner:roll:
Zog, I definitely have issues with NETA, BUT............... I will save them for another post.
Tony