Hello All,
I have a motor (3-ph, 2300V, 300HP, FLA-67.5amp, SF-1.0) constantly running at about 82 amps. Which is about 1.2 times of its FLA. It's used to drive a water pump. The motor has class B insulation. I have checked the amp meter to make sure it's not the meter reading higher. I don't have any flow information thus not able to check pump curve to see any horsepower information. Knowing the SF is 1.0, I thus wonder how bad would it be to run the motor like this. I know that this will make the temperature go up, but I'm not sure how much that will be; and of course we all know that "rule of thumb" is every 10 deg.C increase will halve the motor life. Thus I'm trying to get some advice here.
Also, my thermal protection on this motor is an old GE electromechanical type relay, which is fed by a 100/5 CT, and has thermal setpoint at 3.52 amp on the CT secondary; so that makes it 70.4amps to trip? how come my motor is still running then if that's the case. did I intepret it right?
Thanks.
Thanks.