It certainly could. Often times the machine manufacturer will have a preference.Lets say i have a machine and its full load is 60amps does it matter if i use a breaker or fuse.
And the breaker manufacturer's say that a properly rated breaker will reduce the incident energy of an arc flash greatly versus a fuse.The fuse manufactures say that properly rated fuses will reduce the incident energy of an arc flash greatly versus a breaker.
It can also depend on who you ask..... each "side" can provide you a good sell on their product....
Zog may disagree with me and he is certainly more qualified, but often it appears to me that it comes down to (a) the obvious ability to "reset" a breaker vs changing a fuse; (b) possible greater fault current limitation with fuses in some cases and (c) price, but as he said the discussion could take pages when you consider such things as selective coordination, series ratings, etc.
Sure they do, they sell fuses. They make current limiting fuses the magic cure for arc flash, in some cases they are very effective, in other cases not. What they fail to mention is the current needs to be in the current limiting range to be effective and with arcing currents being lower than bolted fault currents that is often not the case.
Thats why I prefaced my comment with "Fuse manufactures", it just depends on who is selling what.:roll: You sell breakers, right?![]()
(d) Possiblity of a fuse single phasing a load.(a) the obvious ability to "reset" a breaker vs changing a fuse; (b) possible greater fault current limitation with fuses in some cases and (c) price, but as he said the discussion could take pages when you consider such things as selective coordination, series ratings, etc.
(e) communications capability
(f) ZSI
(g) remote operation
(h) Maintenence modes
Not any breaker that would be replaced by a fuse. And I am not making false claims about breakers either.
Zone Selective Interlocking. The ability to preset a system of breakers to isolate a ground fault at the closest possible breaker by having them communicate to each other.not familiar with ZSI. would you mind ?
As my input to this never ending debate, I always like to point out one important fact about fuses.
All of the benefits they can provide go right out the window when someone can't find the right one and replace it with the next size up, or worse yet, a large bolt, a piece of EMT or copper pipe.
I have never seen that happen with a breaker.