Good then I am glad that we are agreeing.
		
		
	 
Me too 
 
 
	
		
	
	
		
		
			No  this is not where either of us are going wrong. I do believe once again  we are in agreement with the exception that you think that Table 310.16  is part of 310.15 which does not happen until 2011.
		
		
	 
No, I don't believe that, I believe that 240.4 requires that conductors  be protected in accordance with their ampacities specified in 
310.15, unless otherwise permitted or required in 240.4(A) thru (G).
	
		
	
	
		
		
			It is in Table 310.16 that tells us to look at 240.4(D) for the ampacity of a #14 conductor. 
		
		
	 
I disagree.  Table 310.16 tells us that the ampacity of a #14 (cu)  conductor is 20, at the 60 and 75 degree temperature rating.  Table  310.16 tells us to refer to 240.4(D) which tells us to protect #14 with a  15A max OCPD, 
UNLESS specifically permitted in 240.4(E) or (G).
Even protected by a 15A OCPD, #14 still has an ampacity of 20.
 
 
	
		
	
	
		
		
			Wow boy am I surprised. All my life I thought that a definition of something was to tell you what that something was.
		
		
	 
 
Me too.  That's why I don't understand why you are trying to say that a  conductor which clearly meets the definition of a "branch circuit  conductor" is NOT a branch circuit conductor.
 
	
		
	
	
		
		
			Is it not you that keeps saying that the ampacity of#14 is 20 amps? 
		
		
	 
No, it is not me who says this, it is the NEC who says this (see T310.16.)  I am just repeating what the NEC says.
  
	
		
	
	
		
		
			Then  how can #14 be a tap on a 20 amp circuit? In order to be a tap it must  be a conductor that has overcurrent protection ahead of its point of  supply that exceeds the value permitted for similar conductors. If the  14 is a 20 amp conductor then it is not a tap on a 20 amp circuit.
		
		
	 
Again, here is where you are getting lost.  As you say, a tap must be a  conductor that has OCPD ahead of its point of supply that exceeds the  value permitted for 
SIMILAR conductors.  A branch circuit using  #14 would be protected at 15A per 240.4(D).  A branch circuit using #12  would be protected at 20A per 240.4(D).  A tap of a 20A branch circuit  could use #14 conductors, because the OCPD of the branch circuit (20A)  would 
exceed the value permitted for 
similar conductors (15A.)  But of course, those taps can only supply the loads permitted in 210.19(A)(3)&(A)(4).
 
	
		
	
	
		
		
			Now  here is where someone is going astray. As outlined in the exceptions  under 210.19(A)(3)&(4) it is very clear that the tap is not the  branch circuit not part of any feeder and this is by definition of both  branch circuit and tap conductor.
		
		
	 
I don't follow.  You say that it not the branch circuit and that it is  the branch circuit in the same sentence?  The definition of a branch  circuit is "the circuit conductors between the final OCPD protecting the  circuit and the outlets."  How does the branch circuit tap conductor 
NOT meet this definition?

  The tap conductors meet the definition exactly.
 
 
	
		
	
	
		
		
			then it is an illegal installation in violation of 210.20
		
		
	 
How is what I described a violation of 210.20? I followed 210.20  precisely.  See post #104.  If I protect my conductors exactly how  210.20 (and 240.4) tell me to, how am I in violation?
 
	
		
	
	
		
		
			Any  conductor that is protected above its ampacity is a tap conductor and in  no way fits the definition of branch circuit or feeder.
		
		
	 
You've lost me again.  Where does the definition of a branch circuit or  feeder say anything about overcurrent protection or ampacity?  They  don't!  The branch circuit and feeder definitions tell us 
WHERE the conductors are installed in the premises wiring system, not 
HOW they are protected.  If the definition of a feeder is '
ALL circuit conductors between the service equipment and the final branch-circuit overcurrent device,' then a feeder tap, which 
IS a  circuit conductor between the service equipment and the final  branch-circuit OCPD, is, by definition, a feeder.  I don't see how it  could be any more clear.
 
 
	
		
	
	
		
		
			The  code mandates how all conductors are to be protected. Branch circuits  must have a conductor that will carry the load served and be protected  accordingly. The same is true for feeders. For conductors under 800 amps  the next higher overcurrent protective device can be used as long as  the circuit is not supplying a multioutlet branch circuit supplying  receptacles for cord-and-plug-connected portable loads.
		
		
	 
Where does the code say branch circuit conductors must carry the load  and "be protected accordingly?"  It doesn't say that.  The code says  branch-circuit conductors shall be protected by OCPDs that have a rating  or setting that 'complies with 210.20(A) thru (D).'  See 210.20.
210.20(B) says those conductors shall be protected in accordance with  240.4.  240.4(E) says that conductors are permitted to be protected at  lower than their ampacity in accordance with 210.19(A)(3)&(A)(4).   Protecting circuit branch circuit conductors at less than their ampacity  is 
ALLOWED by 210.20.
 
	
		
	
	
		
		
			then  pray tell us why they would have a definition for Tap Conductors? A tap  conductor in no way fits the definition of a feeder.
		
		
	 
There is a definition of tap conductors to distinguish conductors that  are protected at higher than their ampacity.  And because there are  rules specific to allowing the installation of these conductors  protected at higher than their ampacities.  For example:  240.21(B)(1)  Taps not over 10' Long.
If the feeder tap conductor is a conductor 'between the service  equipment and the final branch-circuit conductor,' then the tap  conductor meets the definition of a feeder 
TO THE LETTER.
 
 
	
		
	
	
		
		
			and  210.19(A)(3) Exception 1 tells me the criteria that I must follow to  install this range outlet tap. It is not in the main body of the text it  is in the exception. I can wire this cook-top with #12 conductor from  the range outlet to the cook-top 
		
		
	 
What difference does it make that the allowance is in the exception?   The exception exists in the BRANCH CIRCUIT Article, which tells you  about 'branch circuits.'  210.1 Scope:  This article covers branch  circuits except for branch circuits that supply only motor loads...  The  allowable tap to the cooktop from the range branch-circuit is part of  the 'branch circuit' as covered in Art. 210.
 
	
		
	
	
		
		
			from a  box that has conductors protected at 50 amps I am allowed to tap this  outlet with a 20 circuit to supply either an oven or a cook-top that is  in the same room. The Range branch circuit is from the breaker to the  outlet and is rated at 50 amps. Those conductors from this outlet going  to the load being served are taps and are not part of the branch  circuit.
		
		
	 
Yes, you are permitted to tap for the oven or cook top from the 50A  range branch-circuit, per 210.19(A)(3)Ex.No1.  The 20A tap conductors  are still between the final OCPD protecting the circuit and the oven (or  cooktop) outlet.  As such, these conductors ARE a part of the branch  circuit, by definition.
 
 
	
		
	
	
		
		
			So if  I decided to strap this whip to the fire rated ceiling support wire the  inspector could not turn me down. As far as that goes the inspector  couldn?t even look at this whip. Is this what you are saying?
		
		
	 
As far as I know, the installation of luminaires falls within Article  410 of the code, so and inspector certainly could and should look at the  fixture whip.
 
  
	
		
	
	
		
		
			Well  okay then. I suppose that I could wire premises wiring with fixture wire  after all Exception 2 under 210.19(A)(4) starts off with, Fixture wires  and flexible cords shall be permitted.
According to your explanation  these conductors (Fixture wires and flexible cords) would be part of the  premises wiring and part of the branch circuit. This would also mean  that any and all of this wiring would have to fall under the rules of  the NEC. Can?t have it both ways. 
		
		
	 
No, you couldn't wire the entire premises wiring with fixture wire.   Nothing in 210.19(A)(4)Ex.No.2, permits such a use for fixture wire.   See Art. 402 for permitted uses of fixture wire.  All the Ex.No.2. does  is permit conductors smaller than #14 for branch circuit conductors  using flexible cords or fixtures wires in accordance with 240.5.  The  use of a flexible cord or fixture wire would need to comply with  Articles 400 and 402, respectively, and are somewhat limited.  However,  these conductors would still be part of the branch circuit, and part of  the premises wiring system.  This is having it both ways, it is having  it the Code's way.