This is my first time on Mike Holt's forum. I am looking for some help on transformer sizing. I am a little confused about how to handle kva for single phase loads when they are connected to a three phase system. We have 2- 5 ton units that are powered at 208V single phase. The current required to power each unit is about 37 amps. Since the unit is single phase do I calculate the KVA as the following:
37*208V/1000 = 7.7 KVA
2 units @ 7.7 KVA = 15.4 KVA = total connected load.
Will a 20 KVA transformer @ 3 phase be able to take care of this loads?
The maximum full load amps for a 20 KVA transformer is 55.5 amps. But the loads at single phase pull (37*2)= 74 amps, which is more than the 3 phase capacity of the 20 KVA. I am confusing myself thinking about it.
My question is will a 20 KVA be able to handle the load or do I need to calculate the single phase loads as 3 phase loads because they are connected to a 3 phase system? Or do I need to go up to 30 KVA system which is good for 83 amps @ 208/3 Phase.
Your help is greatly appreciated. Thanks guys.
This is my first time on Mike Holt's forum. I am looking for some help on transformer sizing. I am a little confused about how to handle kva for single phase loads when they are connected to a three phase system. We have 2- 5 ton units that are powered at 208V single phase. The current required to power each unit is about 37 amps. Since the unit is single phase do I calculate the KVA as the following:
37*208V/1000 = 7.7 KVA
2 units @ 7.7 KVA = 15.4 KVA = total connected load.
Will a 20 KVA transformer @ 3 phase be able to take care of this loads?
The maximum full load amps for a 20 KVA transformer is 55.5 amps. But the loads at single phase pull (37*2)= 74 amps, which is more than the 3 phase capacity of the 20 KVA. I am confusing myself thinking about it.
My question is will a 20 KVA be able to handle the load or do I need to calculate the single phase loads as 3 phase loads because they are connected to a 3 phase system? Or do I need to go up to 30 KVA system which is good for 83 amps @ 208/3 Phase.
Your help is greatly appreciated. Thanks guys.