T
taylorp
Guest
210.52 (A) gives general provisions for installing receptacle outlets. Kitchen receptacle requirements are covered under 210.52 (B) Small Appliances. Kitchen receptacles are required to be on a Small Appliance circuit, and the NEC says that there shall be two or more for such rooms (210.11 (C)(1).
Walls are treated differently in the Kitchen. 210.52 (B) and (C) explain where to locate kitchen receptacles. In 210.52 (C)(5) it explains that wall spaces occupied by appliances or other stuff are not part of these requirements.
Therefore, I believe that wall spaces behind cabinets, refrigerators, ovens, and the like are not required by the NEC to have receptacles installed in them, but we install receptacles for the convenience. Installing a receptacle behind the refrigerator is a courtesy not a requirement. Nor is it required to put such receptacles in the kitchen on a GFCI.
I have never seen an electrician install receptacles on the kitchen wall only later to have kitchen cabinets cover them up.