jxofaltrds
Retired ESI
- Mike P. Columbus Ohio
- Creator
No response, Mike?
I disagree.
No response, Mike?
Why do I think that it is not wall space? I 'feel' that it is 'in' the cabinet.
If we have a garage on the countertop we are not required to place a recpt. in it. Correct?
Yes.
No.
Yes.
Absolutely not.
Absolutely not: 210.52(B)(2).
Exception 2 to that section makes it clear that the space behind the range is not wall space.
The receptacle behind a gas range is an "other outlet" than a 210.52(A) wall space receptacle. The exception proves this. Thus, a receptacle behind an electric range is something other than a 210.52(A) wall space receptacle.
Yes but the garage has a door and makes it a cabinet.
put a door on this sapace under the counter and we have just that a cabinet.
This is an open wall space that just simply is not as tall as most walls.
I see no exceptions to not call it a wall. If it was half wall or knee wall would you let it pass ?
What i see the space as is a small space with the eqivalant of a shelf over it. Likely to be used NO but NEC does not say usable.
Customer/ owner might say it is for future DW but fact is at time of inspection it has none.
The first graphic shows wall space as desribed in 250.52(A)(2). Tell me what exempts this space. No opinion code article.
The second graphic shows countertop wall space as described in 210.52(C)(1).
The space in graphic 2 below the countertop is not address in the NEC. So if not addressed none required.
I couldn't care less about the space ABOVE the c'top..... I'm addressing the space BELOW the c'top.
Why is it NOT wall space because it's below the c'top?
I will ask again: Where in the Code is a wall below a c'top not considered wall space?
Where there is a cabinet.
Where there is an appliance.
It is not in the code. It is understood.
The code does not require or exempt the wall under a counter from (A)(2).
In otherwords the code is silent.
OK, let's try this angle.... where, in 210.52(A)(2) does it address countertops?
It does not. Just the wall space between them.
So does the 24" space require a receptacle or not?
Now........ why not?
We can not possably go along with it is UNDERSTOOD
The code did cover this space and points it out as along the floor. You have 2 feet of wall and only thing that exempts it is if the space is broken up by something such as fireplace, appliance etc. Yes common sence would say look at blue print and if says DW then fine on rough inspection. But on final we either need a wired in DW , cabinet door, or a receptacle.
I can not justify that. I believe the NEC is silent on this space so I could not require an outlet.Without anything there I simply have wall that is 2 feet and clearly calls for an outlet.
So given that space we see here in picture #2 in my opinion needs a receptacle.
Because that is what the code says.Why can I have a SABC for the dining room and not the range? Silly to run a single circuit but why not?
Right where I told you: 210.52(B)(2) exception 2.Where does it says that the recpt behind the range is an "other outlet"?
210.52(B)(2) says that it cannot, not that it must.It just shows it coming off the counter, it does not say that it must.
How does any of this obfuscation have any bearing whatsoever on our discussion? :roll:If I put my range in my dining room, would that exempt that wall from meeting 210.52(A)(2)?
Nothing in the exception says anything about a wall.
I could put my range in the middle of the room and install a floor recpt for it. Odd installation but compliant. That would leave a 30 - 36" (typical) wall. How would you handle that area with no cabinets or appliances?
Mike says that wall spaces behind appliances require wall receptacles as required in 210.52(A).Please spare me from reading this entire thread. I am not sure what we are arguing.
We are providing a plethora of reasons why this view is in error, but to little avail.