Irrelevant.
It is. 210.52(B)(2) prohibits it.
Logic 101:
An exception (by nature) is going to say something contradictory to the rule that it is attached to.
Exception 2 exists for a reason. I am taking that for granted. If you believe it is wasted ink, that could be the source of our failure to communicate. Without exception 2, 210.52(B)(2) would be prohibiting us from installing any SABC receptacle behind any range.
Let's mess with your hypothetical home after a while. Agreed?
Ken, I am saying that 210.52(B)(2) prohibits installing a SABC receptacle behind an electric range. Agree or disagree?
Ken, I am saying that 210.52(B)(2) prohibits installing a SABC receptacle behind an electric range. Agree or disagree?
Which "it" are you referring to, specifically?This is where we disagree. It 'allows' that outlet to be feed from the SABC.
Please elaborate, I do not understand what you're saying here.It does not say that we can not add one for the range. Yes this would be stupid but allowed.
Show me that exception.Disagree. You install it for a gas unit in the future, even though you know an electric one is going to be installed.
That ties into your hypothetical home - running a dedicated 15A or 20A homerun would be the only argument-free prewire, IMO.Why are we allowed to 'added' it to a SABC but not allowed to supply it from it's own SABC?
Which "it" are you referring to, specifically?
Please elaborate, I do not understand what you're saying here.
Show me that exception.
That ties into your hypothetical home - running a dedicated 15A or 20A homerun would be the only argument-free prewire, IMO.
Ah, okay, thanks."IT" being the exception. #2.
It is for supplemental equipment and lighting on gas ranges. Only. Finis. Caput. End of sentence. It is not as general as you are trying to read it. It is very specific.Exception No. 2: Receptacles installed to provide power
for supplemental equipment and lighting on gas-fired
ranges, ovens, or counter-mounted cooking units.
Ah, okay, thanks.
210.52(B)(2)ex2 is too specific to be used for the electric range wall:
It is for supplemental equipment and lighting on gas ranges. Only. Finis. Caput. End of sentence. It is not as general as you are trying to read it. It is very specific.
Show me that exception.
210.52(B)(2) Exc. 2.
What other reason would you have to install a 120v recep in the range space other than for a gas range?
Nothing there says the range installed TODAY has to be gas-fired. So I installed it for any FUTURE gas range that may go in there.
Since I installed the SABC/recep for a gas range, it's allowed under the exception.
I seriously doubt many people will be pulling their stove out to plug in a toaster or coffee maker. If they did, then I failed miserably when it came to 210.52(C).
George when I finally convince you, you are going to kick yourself.
I would LOVE to see your justification for this.20 AMP only. 15 AMP not allowed.
Sounds like we may be agreeing?
"What other reason would you have to install a 120v recep in the range space other than for a gas range?"
We will do this one on another post.![]()
On my way out the door...
I would LOVE to see your justification for this.
I would have no problem putting in a 20a SABC recep behind an electric range, and would present Exc. 2 to the inspector all day long.
210.52(C).
(1) Wall Countertop Spaces. A receptacle outlet shall be installed at each wall countertop space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.
Exception: Receptacle outlets shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink in the installation described in Figure 210.52(C)(1).
Sounds like we may be agreeing?
"What other reason would you have to install a 120v recep in the range space other than for a gas range?"
We will do this one on another post.![]()