bobby taylor
New member
 - Austin,TX.
what is the min. distance a sub panel can be from waters edge of a pool? [single family dwelling]
			Could be between 6' or 10' depending if any receptacles are attached to the panel or are near the panel.
680.22.
Mike I know you are busy on the 20 threads about recep. in a kitchen but what does 680.22 have to do with a sub panel.
Thanxs I lost count.
IF I had an outlet attached to my 'sub' panel and it was within 6' of the pool it would be a violation.
If that outlet was supplying a pump and within 10' it would be a violation.
5 ft unless seperated by a wall per 680.12, IMO
That is about the best section that I can find but really does not necessarily apply to the OP unless it feeds pool equipment and is the disconnecting means for said pool equipment.
You would think there would be a section someplace that specifies a minimum distance for 'any' electrical equipment, whether related to pool equipment or not, but I don't find one. If supplying pool related equipment there are multiple sections with a minimum distance from the water.
The outlet would be a violation, the question is about the panel.
680.22(D) requires switching devices to a minimum of 5' from the inside wall of a pool. Most panels contain switching devices (circuit breakers or fusible switches).
How is that pushing it? A circuit breaker or fusible switch is a switching device.Thats pushing it a bit. They are not really saying panels
Would say it is not great location for a panel but what would be hazard if not part of pool equipment
had they intended to include panels they would have said it. Not all breakers are listed as switch. I think they simply overlooked it. Could I have a meter can a foot from the pool ?How is that pushing it? A circuit breaker or fusible switch is a switching device.
You don't think standard circuit breakers are considered switching devices? Whatever dude. :-?