Jim W in Tampa
 - Tampa Florida
I agree with Bob
marked it on wall I think we might be at 7
It proves no such thing.
The NEC is not there to prevent installations that offend people. It is there to prevent electrical hazards[/B] and assuming that all other code sections are satisfied there is no electrical hazard in running conduits across a floor.
In fact you find it done quite often around machinery.
The NEC is not there to prevent installations that offend people. It is there to prevent electrical hazards and assuming that all other code sections are satisfied there is no electrical hazard in running conduits across a floor.
...if your going to quote 90.1(A), do not reword it
(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.
...your right, he did not 'quote' that section. My point was to say that a hazard can be created by the installation of conduit that is not really an 'electrical' hazard.
Good day all,
I have a location where conduit has been run across the floor in a electrical room. Can someone direct me to the code where this is allowed or not?
Just doesn't seem right. This is in a jail facilities electrical room.
It would be an OSHA violation of smooth and even surfaces for travel and egress, unless marked and guarded as specified in OSHA' It's a tripping hazard.
It certainly CAN be an electrical hazard when it is the required clearance space where panel access is required.
That is where I jumped to as well.It would be an OSHA violation ... It's a tripping hazard.