paul
- Snohomish, WA
I agree, the NEC shouldn't require a ground wire in EMT, they should ban EMT and require RGS or IMC with threaded connections instead.
That's because a conduit can out-carry any conductors that they may enclose.
Do you think the NEC being the minimum is borderline dangerous?
Allowing exposed SE cable for service conductors comes to mind.
You should qualify your comment by saying that you have no firsthand experience with SE cable and that's only your opinion.
Those of us who do have first hand experience with SE cable and work in areas where it's common know that it's a safe wiring method used in countless installations for decades without trouble.
1. I have plenty of first hand experience with SE cable. It's a fine product when concealed and protected via OCPD's
2. Everything I say is only my opinion. It's is stupid to expect me to preface everything I say with a disclaimer.
3. I've also never installed bare split bolt connectors to extend wires in a panel but I KNOW it aint safe.
4. I could go on forever but, if you don't understand my point, you never will.
There are a lot of electrical installations that have been in use for decades. Just because it's common doesn't make it safe.
Just because you use this method doesn't mean you know anything. Yours is simply another opinion.
This from the guy that says the code should use commonsense.
What would be the commonsense of banning a method that has a huge history of safe installations?
You want to ban a method because you are sure it is bad but history proves you are mistaken.
Fear is not a reason for a code rule.
You are right, just the fact it is common does not make it safe.
But the fact that is very common and has not left a trail of burned properties and dead homeowners does say a lot.
Show some proof it causes more fires or more injuries than you might have a reason to want it restricted.
Again if it was just me and Pete using it you would have a point, but I can drive past 100s of SE services in my own town never mind my county, or state, or region.
If SE was as dangerous as you seem to think it is electricians in this area would know about it because we would be replacing them
yeah but mine was dumberUm, cause it was just a dumb joke maybe????
Add a little corrosion, moisture to build up resistance inside the wirenuts and connections and the wire conductor will not be what it once was either.
Roger
Installing a EGC in EMT is a great way to go above and beyond.
In real life corrosion of copper wires usually only occurs when aggressive chemicals are present.
The copper connectors are designed to be flexible and to maintain the pressure under the thermal cycling.
And these extreme conditions exist inside all bldgs? Hmmmm, maybe someone should let the authors of NFPA 99 and CMP #15 know this, they could then change 517.13 and especially 517.13(B) Exception No.2.The steel and iron used for raceways are attacked by atmospheric moisture.
This comes from the person that uses sheet metal screws to ground old metal boxes with no threaded holes, interesting.
And, the installation is 100% secure. If you want to meet for lunch in Central Phoenix, we can stop by, pull it apart and tug on it. For a real adventure we can even short it out .