So what does the code say to do when there is no ground wire? Pig tail from the box or ground to the cover plate screw which is acceptable?
So what does the code say to do when there is no ground wire? Pig tail from the box or ground to the cover plate screw which is acceptable?
Read 250.146
Roger
See 250.8, you will notice that cover screws are not listed?What about a 4 square junction box with no outlets just splices, do i use a pig tail or ground to the box cover screw?
j-boxes where not designed to ground at the ring cover screws... and your answer would be pigtail from a green machine screw in the back of the box
This is being picky
It is what we do here. :grin:
Besides, as you said there is no requirement for a green screw.
What is EGC? If you can use EMT as a ground, then why is a ground wire required by the NEC, assuming it is.
External Grounding Conductor?
Again if it was just me and Pete using it.....
And you know this from all your years out in the field servicing electrical installations. ...:grin:
I find corroded copper conductors in any location that they get wet, particularly under the steel spring of a wirenut.
Next time you run across one of these look very closely at the actual interface points between the copper conductors. You may find that they are somewhat tarnished but the corrosion does not extend to the actual electrical connection.
In real life corrosion of copper wires usually only occurs when aggressive chemicals are present.
And you know this from all your years out in the field servicing electrical installations. ...:grin:
Yep, about 40 years.
The copper connectors are designed to be flexible and to maintain the pressure under the thermal cycling.
I have found the same. While humidity alone is not a corrosive agent, it tops the list of variables that are important to the corrosion process. Reactive chemicals are close to the top and temperature is near the bottom of the importance stack. To state the obvious to some, you will find that, as a general rule, copper tarnishes at a much faster rate in industrial environments.I find corroded copper conductors in any location that they get wet, particularly under the steel spring of a wirenut.
I don't have a link but I will tell you that copper connectors are indeed designed to give better mechanical characteristics. Copper alone has poor spring properties, but by adding beryllium (less than 2%) or phosphorus, you can get a very good spring connector. These are also good up to around 150?C. Belleville washers are usually made of steel but you can get them made of bronze and copper alloys.I am still waiting for those for a link to these ...