jhsugg
I am dealing with an existing utility owned/maintained combo meter socket and panel installed in the late sixties or early seventies. The house is being sold and a home inspector noted on his report there were 9 breakers in the panel without a main breaker which violated the 6 breaker limit. The panel originally feed 2 sub panels, a water heater, dryer, a cook top, and a wall oven. One of sub panels served the 220 volt baseboard heat throughout the house and the other panel served the home's 120 volt circuits. Due to remodeling and other modifications over the years, the 220 volt sub panel for the old baseboard heat was abandoned and disconnected and a single unit heat pump was added along with other changes etc. Due to the current configuration,  it would be very cost prohibitive for the seller to have to incur the cost of rewiring etc in order to get the number of breakers down to 6 just so they can  sell the home.
Section 408.36 in the new 2011 NEC states ?In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.. Exception No. 3 states: ?For existing panelboards, individual protection shall not be required for a panelboard used as service equipment for an individual residential occupancy.
My question is this, can Section 408.36, exception #3 be interpreted to mean an existing residential panel (the one I'm dealing with) have more than 6 breakers without an overcurrent protective device having a rating not greater than that of the panelboard (main breaker)?