Solar PV Grounded Conductor Identification
stevee
Does the grounded conductor of a DC output circuit have to be identied by the color white or grey as required in NEC 200.6?
Is it permissible to use a colored conductor, let's say black for the grounded conductor?
Does the color identification apply to the source circuit conductors also?
Grounded conductors must be white or gray regardless of AC or DC and regardless of the polarity.
It the conductors are 4 AWG or larger you can re-identify them to white or gray.
I agree with Bob.
Just curious, do you have an actual grounded conductor in the DC output circuit?
Most of the PV systems that I have inspected do not have a grounded DC output circuit.
In fact I have made installers remove the white #10 and replace it with another color because the DC output circuit was ungrounded.
Chris
I agree with Bob.
Chris
In most if not all of the PV systems I've seen the PV output circuits have been grounded at the inverter. These generaly are bonded to the grounding electrode conductor through the Ground Fault Protective device as indicated in 690.42 exception
The systems that I have dealt with have been ungrounded as permitted in 690.35.
Chris