Rick Christopherson
Like Don, you are getting hung up on names and/or colors; as opposed to functions.I doesn't?
The first part of Don's quote is talking about previous code allowing the neutral to be used as the grounding conductor, no differant then at a service.
The second part of Dons post is talking about the 2008 removal of this allowance and the requiring of a seperate EGC ran to other buildings, so this EGC would not be current carrying like the neutral would in Dons first part of his post, and he pointed out this EGC would most likly be smaller then a neutral that was allowed pre-2008.
If you have a ground-to-neutral bond at both locations, then you have parallel conductors, and both of them will be current carrying conductors. Electrons are color blind. They don't care whether they are flowing down a green colored wire or one that you choose to label "EGC". Parallel paths (e.g. ground loops) completely negate the EGC between buildings. You have 2 grounded conductors, and 0 grounding conductors. They both carry "normal" current.
If you are going to carry the EGC from one building to the other, then only one building can have a G-N bond. The exception to this is a separately derived system using an isolation transformer. However, this leads to the next point....
You indicated that it was required to bond across a transformer. If you bond across an isolation transformer, then it is no longer a separately derived system. This negates the very purpose of the isolation transformer. To say that it is required to bond across a transformer, means that there is no such thing as a separately derived system, unless of course we are referring to off-grid generators.By the requirements in the NEC you would still be required to bond across the transformer and still have the voltage problems in building A don't look for band aids to fix a real problem.
By this statement, you have wiped out the very nature of a separately derived system. Does this mean we can strike those words from the NEC?![]()
An isolation transformer is in fact a valid solution (not a band-aid) however, as the OP already stated, not very cost effective.