- Windsor, CO NEC: 2017
- Service Manager
Where would I find a requirement for locating a disconnect on the line or load side of a typical 480 - 120/208Y transformer supplied by a 150A primary breaker?
450.14 Disconnecting Means. Transformers, other than Class 2 or Class 3 transformers, shall have a disconnecting means located either in sight of the transformer or in a remote location. Where located in a remote location, the disconnecting means shall be lockable, and the location
shall be field marked on the transformer.
an absurdly simple question from you scares me more than a snake:grin:
both may bite you....
Would 240.21(C) not cover the need and location for a secondary disconnect.
Under '08 and earlier, there is no requirement for a primary disconnect.
There has never been one as far as I know up until the 2011 NEC and that is at the office.
How about this for 2011-- all new
Does that strike anybody else as odd? All these years, no requirement to have a disconnect on a transformer?
It was added in the opinion of increasing the level of safety for qualified electrical workers who may need to work on or perform maintenance on the XFMR. Sounds like a smart move to me. This change simply brings XFMRs in line with similar requirements for motors, generators, appliance and so on.
So in other words, 'Just because' without and real issue being used to substantiate the need.:roll:
No more than for any other piece of equipment.
If one is not needed for a transformer then why would one be needed for any other piece of equipment?
Some where some how common sense comes into play.
Substantiation: Requiring a disconnecting means for a transformer is intended
to enhance safety for the qualified individual that is required to work on the
transformer. This is especially true in installations utilizing the requirements of
240.21(B)(3) whereby there may be several transformers in different locations
all tapped from one feeder and it may be impractical to de-energize the entire
feeder system to work on one of the transformers.
It is not commonsense to make a rule just for the sake of making things 'the same' the equipment and needs of the equipment are very different.
Like motors? Which often require service and have moving parts.
Like appliances? Which often require service.
OTH transformers do not often require service and the people who would be serviceing transferomers would presumable be well quilifed and know they are required to do LOTO back at the source.
Exactly and this new code section lacks all traces of it.
There is no evidence contained in that substantiation that this has actually been a problem.
As far as things being 'tapped from one feeder and it may be impractical to de-energize' that clearly sounds like a design issue.
That same argument could be used to justify everything from mains in every panel to reducing the amount of circuits allowed in each panel.
450.14 Disconnecting Means. For transformers other than Class 2 and Class 3, a means is required to disconnect all transformer ungrounded primary conductors. The disconnecting means must be located within sight of the transformer unless the location of the disconnect is field-marked on the transformer and the disconnect is lockable. (click here to see Fig. 17)
Analysis: Although many Code users have believed that this requirement already existed, in previous NEC editions transformers were one of the only pieces of equipment that didn?t require a disconnecting means. Although there were no documented injuries to warrant this change, it?s hard to argue that this requirement doesn?t enhance safety.
Something than never seems to be considdered with the NEC.... but requiring ?safer? over ?safe? should also include a sound economic justification.
Now this of course in nothing more than your opinion, is it not?