No two PV systems are alike, so $/watt is just for ballpark numbers. Here in east Tennessee I have to deal with a dozen or so utilities, all of which have their own requirements, from engineering, through inspections, and metering, disconnects. therefore, an identical PV install in one utilities jurisdiction can have a vastly different cost than the neighboring utility.
Other factors to consider, roof material, height, distance to inverter, etc. We just finished a 2kW ground mount system that we had to custom make the ground mount out of structural aluminum, because the roof was earthen and the depth varied from 2'-6' and no additional weight for ballasting was allowed.
Also, PV supply prices can fluctuate based on supply and demand, we do not quote an install before getting an equipment quote directly from our distributor, because of pricing and availability issues.
We use the $/watt as an internal gauge only as a check to see if we may have missed something before presenting the proposal to the customer. We also provide the entire service from design, through engineering, submittals, installation and inspection, then commissioning. We did one system where we connected the metering only, but our concern is that our company name is on the TVA contract right along with the customers, and when the roofer, carpenter, handyman, painter, plumber, or whomever installs the wracking and array is long gone, guess who gets the call for any problems with their work?
TVA currently only allows what they call "option 2" to be used where we have to feed into a separate meter to calculate the generated electricity. In some areas you can back feed a breaker in the existing panel and the existing meter will calculate  the difference between usage and generation.
Instead of pricing by the watt I highly recommend reviewing the scope and pricing the same way that you are set up for other service change type of work, etc.
690 is like 680, not every EC does this kind of work, and not every EC should do this kind of work!
I'm with Bob on the OSHA stuff, we now own all sorts of fall protection equipment that we probably should have been using for years.
Good luck with your estimate!