And, if the conductor is loose and the bolt has not turned, does it just stay loose?My preferred approach is when the bolt is initially tightened and torqued, use a sharpie and put a line from the bolt to something stationary. Then visual inspection is all that is required to know that the bolt (or nut!) hasn't undone itself.
It would. Thus marking the bolt position is only useful when you know the arrangement is correctly torqued. This can preferably be done either at installation, or some time later when it gets re-torqued. re-torquing = bad, thus doing it once and then marking up saves future re-torquing.And, if the conductor is loose and the bolt has not turned, does it just stay loose?
Electrical connections are subject to continuous thermal cycling as current/heat goes up and down. Since all materials expand/contract with temperature changes, electrical connections are designed to compensate for it. In some cases the material itself is capable to 'follow' and 'spring back' to its original form like bronze and other copper alloys do but as it was found out aluminum does that poorly. Belleville washers were introduced as the device that can provide the longest compensation capability, but of course it is necessary that the proper initial tesion is provided, hence torqueing requirement. Simple spring washers can also provide the same tensioning, returning tension, but depending on the material and the temperature differences and the number of cycles it is subjected to (10^n) it is subjected to, it will eventualy loose its modulus and the heat runaway occurs. The method is called thermal compensation.I am not engineer but understand a little bit of what you gentlemen are saying. As far as electrical connections are concerned....
It is odvious if the connection has burned we cut back the wire and even replace the lug if needed. I notice when a conductor has been tightened, not necessarly torqued, as I'll bet most electricans do not use a torque wrench, the connector leaves a "dent" in the conductor. I think this would leave a week spot in the wire. Just as a torqued bolt could stretch a little making it weak. It has always been my thought, correct or not, that a properly torqued connection will not loosen up. Just going around and tightening even with a torqueing dosen't seen right as the connection maybe too tight already, squeezing the wire too much and streaching the fasenter too much. Typicaly, I go around and just tighten connections and find many loose but that is not using a torque driver. maybe the best process is to use a torque driver when I di this and call it "the best I can do."
Adding the oxide inhibitor where it was not installed by the lug manufacturer will increase the pressure on the conductor if you tighten the set screw to the manufacturer's listed torque. This may result in a poor connection. Too much pressure on the conductor is just as bad as too little in terms of the long time performance of the termination.on larger aluminum lugs -2/0 and up- I really like to back them most of the way out and put a little oxide inhibitor on the threads. this makes them Much easier to back out later, and it doesnt feel like the aluminum threads are galling themselves when tightened.
I love finding the older meter cans around here with the two screw lay-in lugs - they Always have NoAlOx on them and they are a breeze to remove and reinstall
Adding the oxide inhibitor where it was not installed by the lug manufacturer will increase the pressure on the conductor if you tighten the set screw to the manufacturer's listed torque. This may result in a poor connection. Too much pressure on the conductor is just as bad as too little in terms of the long time performance of the termination.
Laszlo,
If the oxide inhibitor is placed on the threads of the set screw, (my understanding of what the poster was doing), it will act as a lubricant and will increase the crushing pressure on the conductors, assuming that the manufacturers torque value was based on dry threads. I would think that in the absence of factory applied lubricant to the set screw threads that the torque value would be based on dry threads. The same amount of torque applied to lubricated threads would result in increased crushing pressure on the conductors.
Laszlo,
If the oxide inhibitor is placed on the threads of the set screw, (my understanding of what the poster was doing), it will act as a lubricant and will increase the crushing pressure on the conductors, assuming that the manufacturers torque value was based on dry threads. I would think that in the absence of factory applied lubricant to the set screw threads that the torque value would be based on dry threads. The same amount of torque applied to lubricated threads would result in increased crushing pressure on the conductors.