perhaps more than you wanted to know.....
perhaps more than you wanted to know.....
A) CalFire requires the home have 10,000 gals on hand, unless you have city water. This house will have 20, really 30 if you include the rainwater tank, and 40+ if you count the pool. (CalFire does NOT, based on bad experiences...)
B) Califunny requires sprinklers in all new construction, and Santa Cruz County did so before the state requirement. This per NFPA 13D.
Further, since they soon found out no homeowner would ever maintain a fire pump; they require the sprinklers be fed off the potable system, with no valve to shut them off without also ixnaying the house H2O. (If you have enough static head, no pump is needed...) They also require spare heads and a wrench be on-site.
Since the sprinkler GPM requirement is far more than most domestic use; the SOP has become packaged VFD-driven systems, aka "Aquaboost" or competitors. They go into high speed when a few heads open. Our pump is ~30 ft below the tankage.
C) I can find no special requirements for backup power for the 13D pump, or other such rules. The Fire Marshal confirms that. Nevertheless, we will have the pump on the Priority 1 panel, where it gets fed by 20KW of backup inverters; those recharged by the solar array &/or a pad-mounted 25KW propane generator. THAT is backed up by a PTO-driven generator on a Diesel tractor.
D) This 13D pump is separate from my discussion on pump disconnects. THAT is about the 670 ft down, 2HP, 480v3ph. well pump that refills those 20K worth of tanks. (Well, it and the other well, driven by a solar array...)
E) As for fire streams, there's a 4" line from the tanks to the wharf-head hydrant, & it must be between 50 & 150 ft. from the house, and from 6-8 ft from the road, with a turnout for other apparatus to pass the engine at the hydrant. It shall be marked with a blue dot, etc. You can get started
Here, if you are bored....