Sorry, I meant the style of the breaker.It is a Type -SO. Sorry about the bad picture
Sorry, I meant the style of the breaker.It is a Type -SO. Sorry about the bad picture
The K family of breakers are in obsolesence. If this is a new I-Line panelboard it will probalby have Powerpact type H, which do not have adjustable magnetic settings, even up to 150A.If my memory serves me correctly, Square D KA Frames do have adjustable trip.
If so, as Jraef, mentions, you can possibly adjust the trip to withstand the inrush.
I do not know what effect that might have on your system coordination.
Your memory serves you well...If my memory serves me correctly, Square D KA Frames do have adjustable trip.
If so, as Jraef, mentions, you can possibly adjust the trip to withstand the inrush.
I do not know what effect that might have on your system coordination.
Tripping System
Square D? thermal-magnetic molded case circuit breakers have a permanent trip unit that contains a factory preset thermal trip element and a magnetic trip element in each pole. The thermal trip element is rms sensing. In circuit breakers with frame sizes greater than 100 ampere, the magnetic trip element is field adjustable. A single adjustment simultaneously adjusts the instantaneous trip point in each pole.
J
So, like jraef said, your breaker needs to be have a minimum magnetic/instantaneous setting of 900A.
These are the design specs for this particular (EE75T3H) transformer since 2009. Your Square D rep should be able to provide it to you.Jim where did you get this from ? Sq D web site?
Second is this typical or worse case current. In field measurements I have generally seen 4-6 times, unless it is an out of phase transfer on a ATS.
I located Square D's 2004 PDF that covers that breaker, and it does say it has a field ajustable mag pickup from 625 to 1250, but I can't find anything saying how to adjust it? as I see no ajustments on the breaker.
Here's the link to the PDF:
http://ecatalog.squared.com/pubs/Ci...uit Breakers/KA-KC-KH-KI/0601CT9101R12_03.pdf
63 amp load inrush calculates to around 110 amps nominal, a weak breaker will always trip on the low scale. A 125 breaker low scale always defaults to 80% which is 100amps. This is lower than the calculated inrush, hence your nuisance tripping.
Another issue is that a fuse is rated different than a breaker for percentage of overload resistance.
Way to much confusing statements.63 amp load inrush calculates to around 110 amps nominal, a weak breaker will always trip on the low scale. A 125 breaker low scale always defaults to 80% which is 100amps. This is lower than the calculated inrush, hence your nuisance tripping.
Another issue is that a fuse is rated different than a breaker for percentage of overload resistance.
Another issue is that a fuse is rated different than a breaker for percentage of overload resistan