jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
I am just not as sure as that as you are, which is fine, we all read things differently.
If the installation is like the one in the Mike Holt graphic he has a 312 amp feeder regardless of continuous on non-continuous loads.
The transformers max rated output is 312. (And I already said this)
That is the OPs problem: How do you tell a clueless customer that he has a 312 amp feeder for a 400 amp panel?
Customer looks at pic/specs and says " I said I wanted 400 amps and WTH is a feeder? Is that the wire going to the fuse box?"