Isn't it odd that there is a requirement for a receptacle within 25' of HVAC equipment
Isn't it odd that there is a requirement for a receptacle within 25' of HVAC equipment, but no similar requirement for a receptacle to be available to service electrical equipment??
Some test equipment: Some types of power analyzers for exampleWhat do you use to service electrical equipment that needs 120v?
What do you use to service electrical equipment that needs 120v?
Some test equipment: Some types of power analyzers for example
Well, you want power available, and light, while you work on the electrical equipment .... but you also want the power off while you work.
Looks like the electric room needs candle holders and the electrician needs an 'egg beater' drill.![]()
Thats so the AC guy doesn't take a rec with a pigtail attached and hook it up to the disco for power. (using the EGC as the grounded conductor)
What do you use to service electrical equipment that needs 120v?
What do you use to service electrical equipment that needs 120v?