What is the code on boat docks and grounding docks?
The current determines the harm.it wasn't enough voltage to cause a "problem".
This is not something Iam working on. But the power co that is generating power told a guy to take the ground wire lose to stop the shock.
G._S._Ohm said:The current determines the harm.
Try measuring the voltage across a 300 ohm resistor wired from the water to the ground. A chunk of hardware cloth with the surface area of a human body attached to the submerged end of the resistor may give you a different reading.
I don't guess around unless I say "I'm guessing."Why in God's name would you guess around at what could potentially kill someone,
and what you reckon would probably just hurt like hell,
and shoot for just hurting people?![]()
CODE VIOLATIONS
1. January, 1994 Oklahoma State Department of Health (OSDH) inspected eleven commercial docks and five private docks, and an earlier (1989) inspection of 116 commercial docks, found 96% not in NEC compliance; most common fault was open ground.
I don't guess around unless I say "I'm guessing."
The effect of current levels on the human body are well documented.
I'm not shooting for anything.
Your comments are not "ad hominem", but they may be "straw man" or they may be just plain
http://en.wikipedia.org/wiki/Eristic
While in general that it true, but it is not true for people in the water where the current is applied across most of the body. This issue if the reason for the pool perimeter bonding...to make sure the water and the surface around the water is at the some voltage. Small voltage differences can prevent people from getting out of the water. Voltage differences that you normally can't even feel....
The effect of current levels on the human body are well documented.
...
You shouldn't be able to see, smell, or feel your electricity unless something is wrong.
In cases of pools, docks and other like locations I don't agree. We are required by the code to energize the water. The voltage that energizes the water is not always from a problem in the electrical system.You shouldn't be able to see, smell, or feel your electricity unless something is wrong.
I know you're right but I usually get a laugh when I say that line to a customer, thought I'd try it on the internet.In cases of pools, docks and other like locations I don't agree. We are required by the code to energize the water. The voltage that energizes the water is not always from a problem in the electrical system.
Often it is nothing more than the normal voltage drop on the utility primary grounded conductor and on the service grounded conductor. This normal voltage is very difficult to eliminate and is the very reason that we have the perimeter bonding rule for pools. We have to energize the pool perimeter to the same voltage as the water to make it safe to get out of the water.
Maybe I'm a little slow, but where is the voltage coming from? Is the equipment picking up voltage from the motors or lights? I've never done any work at docks or boathouses, so this is foreign to me.
If gounding is the problem, can ground rods not be driven into the lake or river bottom? Or would that worsen the problem in the event of a fault current?
Adding a ground rod would put another resistor in parallel with the one we're trying to protect (the person). It may have the appearance of working (if it has much effect), but it would be more accurate to say it would "mask the problem somewhat."That would work, but the most common solution on the utility side is to pull in another phase which reduces the neutral current.