kwired
Electron manager
- NE Nebraska
- EC
..The ground around the house is all rock and the power plant ground puts power in to the lake. with very little dirt to ground, this is a promblem all around the lake. The land around the lake is very rocky.
And how is this different from how a typical concrete swimming pool is constructed other than we don't have equipotential grounding grid intentionally installed in the lake?
Most often the problem is from the utility neutral. They use the same conductor for neutral and ground. It results in the dock becoming part of the neutral return path...
The problem is that you have a certain potential at a particular point at the lake. Then you take the EGC for the electric equipment on the dock and put it in close proximity to the lake. Remember that the other end of this EGC conductor is connected to earth someplace else that will be at a different potential than the water in the lake. By tying it to metal parts within reach of the water you now can touch both points at same time subjecting you to whatever voltage difference there is. A grounding electrode near the dock will bring the voltage from the water to the EGC much closer to zero than if the nearest GEC is hundreds of feet away. If dock is fed by a service or feeder it should have a grounding electrode anyway.