This is hypothetical. Not a hard question but very curious one, IMO
This is hypothetical. Not a hard question but very curious one, IMO
Did you intend for your statement of the problem to say that the load was 355 amps? At 350 amps, you can use 600 MCM under both the 2008 and the 2011.. . . that means 600 KCM according to the 2008 and 700 KCM by the 2011.
Did you intend for your statement of the problem to say that the load was 355 amps? At 350 amps, you can use 600 MCM under both the 2008 and the 2011.
Nothing in the statement of the problem included information about the breaker. The phrase "400 amp service" does not give us that information. Indeed, all it tells me is that the utility equipment (transformer, meter) have sufficient capacity to allow me to install a 400 amp breaker on my main panel. But if the load is 350, and if I use 600 MCM copper, and if I use a 350 amp breaker, I have an acceptable installation that falls within the description of the problem.Not on a 400 amp breaker. 240.6(A)