Alwayslearningelec
- NJ
- Estimator
Ok to splice #10 wires in a jb I know you just use wire nuts. What about splicing 2/0, 3/0 etc. Split bolts etc??? It for tapping a feeder. Thanks.
Do any of your jobs have specs.?
You could :
split bolt
power block
crimp
polaris tap
LB???? Elbow??? That section deals with conductors in boxes etc. What are you saying? Thanks.You need to look at 314.16(C).
Very unlikely your LB will fit the requirement.
easy grasshopper, don't overload it
314.16 number of conductors in outlet, device, and junction boxes, and conduit bodies.
(c) conduit bodies.
Do they come with an installation wrench?Ask the counter guy in the supply house for 750MCM wirenuts.