if you upgrading a service panel from 100amps to a 200amper you have to take out the 2awg feeders and replace them with 4/0 alm ..but do the ui guys have to bring a higher awg service drop or is it already sized for such an occasion
 
if you upgrading a service panel from 100amps to a 200amper you have to take out the 2awg feeders and replace them with 4/0 alm ..but do the ui guys have to bring a higher awg service drop or is it already sized for such an occasion
It's entirely up to them........sometimes they do , sometimes they don't. Also make sure your socket is rated for the new amperage and the riser is the correct size (if you have to install the riser).
 