Not a requirement of the NEC.Ground rod to be flush.
Not a requirement of the NEC.
FYI -Also appears the clamp on ground rod is installed incorrectly.[110.3(B)] I can't 100% tell but it appears that it needs to be flipped around so the NIPS are against the rod.
As an electrical inspector I would not hassle this person because the ground rod was ~2" above grade; placed where it is I feel it is protected enough from probable damage.
I agree with the 250.64(E)....but there is also the 250.70 issue...that pipe clamp used on the rod has zinc screws - thus is not rated for direct burial....because it is outdoor and at grade the zinc screws do rust through [at least they do in my area]. If these screws were stainless there would be a tag on the fitting.
The issue with an 8' rod is not because of the exposed part might be damaged, it is because code states it must have 8' in contact with Earth 250.53(G).
If a guy buries the rod 8' [thus the acorn is below grade] then an inspector wants him to dig it up to see the connection...
I generally leave the top few inches of the hole uncovered. The inspector or owner can mulch over it.![]()
I generally leave the top few inches of the hole uncovered. The inspector or owner can mulch over it.![]()