bonding across a bolted pipe flange

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What's bolted to the flange another flange? If so, then IMO nothing is required. A water meter would be a different story.
 

Ranger86

Member
Location
Las Vegas, NV
The water pipe is not being used as an electrode and the pipe flange is use to connect one pipe to another pipe (like a coupling in the electrical world).
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I can't find the code section that says to put a bonding jumper accross a bolted water pipe flange ....

It is not a NEC requirement.

However it was not an unheard of specification requirement for equipment located in hazardous areas back when I was reading dozens of such specs a year.

I never did get why it was considered to be a good idea. It seemed to me that the bolts were quite an adequate bond.
 